I have a question regarding alarm cable. Fire Alarm & Signal (FAS) cable is made in four varieties: FAS60, FAS90, FAS105 and FAS200. The numbers, I believe, reflect the maximum temperature that the cable will support signal.
FAS60 is very common in the US; Canada seems to be FAS105.
Is there any reason for this, or is it just what's commonly available? In other words, if a cable is CSA-listed as FAS60, can it be used in Canada in a fire alarm application, or must an FAS105 be used?
Thanks in advance for enlightening me!
Mike K
Fire Alarm Cable question
Forum rules
Blatantly advertising your services is strictly prohibited. Violators will be banned from posting. Identification with a company engaged in providing fire equipment service is encouraged in order to validate responses (i.e. a "tag line" which states your name, company's name and contact information is allowed).
Blatantly advertising your services is strictly prohibited. Violators will be banned from posting. Identification with a company engaged in providing fire equipment service is encouraged in order to validate responses (i.e. a "tag line" which states your name, company's name and contact information is allowed).
-
- Site Admin
- Posts: 71
- Joined: Sat Aug 23, 2008 9:10
- Location: Vancouver, B. C., Canada
- Contact:
Re: Fire Alarm Cable question
Actually the numbers refer to the maximum allowable conductor temperature. The conductors will "support signal" for as long as there's a connection (regardless of the temperature). I think you have to worry about what's happening to the insulation at the various temperature ranges since it's manufactured to the tolerance specified on the jacket. FAS105 seems to be a fairly common mark in Canada. All of the cable suppliers I talked with say it's the only rating they stock. I'll have to check CEC 2012 to see if there's a specific reference. None of the guys I talked to could provide me with the chapter and verse. 