Blatantly advertising your services is strictly prohibited. Violators will be banned from posting. Identification with a company engaged in providing fire equipment service is encouraged in order to validate responses (i.e. a "tag line" which states your name, company's name and contact information is allowed).

AWM Conductor Use

Postby Wibber » Tue Dec 07, 2010 10:32

Is AWM conductor suitable for a fire alarm install? Installed in conduit for the initiation circuit.

Some AWM is labelled AWM/TEW, which would be okay via Table 11.
Wibber
 
Posts: 6
Joined: Mon Jul 26, 2010 7:53

Re: AWM Conductor Use

Postby FIRETEK » Fri Dec 10, 2010 7:35

I don't believe it would be. Here's UL/ULC's "take" on it. "Unlike most wire categories, appliance wiring material (AWM) is a Recognized Component used in UL Listed or Classified end products. AWM wires are intended as factory-installed or factory-provided components of complete equipment submitted for investigation, rather than for direct separate installation in the field." (http://www.ul.com/global/eng/pages/offe ... eandcable/).
Frank Kurz
http://www.firetechs.net
1 (888) 340-3473
FIRETEK
Site Admin
 
Posts: 69
Joined: Sat Aug 23, 2008 9:10
Location: Vancouver, B. C., Canada

Re: AWM Conductor Use

Postby sparky » Mon Dec 13, 2010 1:55

Actually if they are TEW conductors and they are 16 gauge they are approved to be pulled in a raceway for FIre Alarm Systems. I would suggest tho to not take my code review as gospel and review the exact circumstance with your local electrical inspector. Although I can't imagine those conductors would be very cheap... :)
sparky
 