Blatantly advertising your services is strictly prohibited. Violators will be banned from posting. Identification with a company engaged in providing fire equipment service is encouraged in order to validate responses (i.e. a "tag line" which states your name, company's name and contact information is allowed).

Regarding Fire Alarm Batteries

Postby Zeus » Mon Jun 05, 2017 1:43

Hello All,

I have a question about replacing fire alarm panel batteries and wanted to ask for your opinion. If for example, a panel takes 2 x 12V40Ah batteries and it is hard to find replacement batteries with the same amperage, would I be able to swap for 2 x 12V42 or 2 x 12V35Ah batteries? Or anything close to 40Ah?
Zeus
 
Posts: 4
Joined: Mon Dec 12, 2016 6:39

Re: Regarding Fire Alarm Batteries

Postby FIRETEK » Thu Jun 08, 2017 4:42

The size of the batteries must never be less than the capacity you calculated in your testing. You're free to upsize or downsize them as long as you're able to confirm that you have the required supervisory and alarm times mandated by the Building Code. Don't forget you also need to add the de-rating factor specified by the manufacturer.
Frank Kurz
http://www.firetechs.net
1 (888) 340-3473
FIRETEK
Site Admin
 
Posts: 69
Joined: Sat Aug 23, 2008 9:10
Location: Vancouver, B. C., Canada