Paper work for verification on one device

Discussion of verification issues and procedures.

Paper work for verification on one device

Postby Frank » Thu Feb 20, 2014 3:04

Hello everyone,
Conducting verification on an added smoke detector. Tested new smoke detector and devices on either side and EOL for open, short, and ground.
My question is do I have to fill out CAN/ULC s537-04 appendix ''C'' or can I document the verification of the device on my work order.

Thank you.
Frank
 
Posts: 11
Joined: Tue Sep 03, 2013 4:36

Re: Paper work for verification on one device

Postby FIRETEK » Sat Feb 22, 2014 9:51

I'm assuming the added device was installed by an electrical contractor under a properly issued permit. I'm certain that the AHJ will be expecting something a little more than just a work order. You need to complete an Appendix "C" form. You need to document the functions that are affected by the installation at the control panel. You also need to perform your battery testing.
Frank Kurz
http://www.firetechs.net
1 (888) 340-3473
FIRETEK
Site Admin
 
Posts: 69
Joined: Sat Aug 23, 2008 9:10
Location: Vancouver, B. C., Canada


Return to Verification of Fire Alarm Systems