Covering End of Line Resistors.

Covering End of Line Resistors.

Postby GlenatOTL » Thu May 18, 2017 7:44

Hello,
About a year ago I asked if it is allowable to cover the boxes containing eol resistors in a high-rise building. In our situation this would occur if valances were installed in a hallway renovation project.
The answer was no because they need to be opened and physically inspected/tested annually. I now can't find any reference to this issue on this site. Has this rule been changed in any way?
Thanks, Glen...
GlenatOTL
 
Posts: 2
Joined: Mon Oct 24, 2016 12:31

Re: Covering End of Line Resistors.

Postby FIRETEK » Sat May 20, 2017 11:35

The answer to your question is in this FAQ (which I'll update with the actual Clause reference, shortly). http://www.firetechs.net/faqs/fire_alar ... .asp#FAI33
Frank Kurz
http://www.firetechs.net
1 (888) 340-3473
FIRETEK
Site Admin
 
Posts: 69
Joined: Sat Aug 23, 2008 9:10
Location: Vancouver, B. C., Canada

Re: Covering End of Line Resistors.

Postby GlenatOTL » Sat May 20, 2017 7:07

Thank you very much for your reply. I looked through faqs, but somehow missed it.
Thank you again. Glen...
GlenatOTL
 
Posts: 2
Joined: Mon Oct 24, 2016 12:31

Re: Covering End of Line Resistors.

Postby FIRETEK » Sun May 21, 2017 7:45

No problem. There's a lot of them. Easy to miss... :)
Frank Kurz
http://www.firetechs.net
1 (888) 340-3473
FIRETEK
Site Admin
 
Posts: 69
Joined: Sat Aug 23, 2008 9:10
Location: Vancouver, B. C., Canada