Annual Fire Inspection Class A Testing

Open forum for questions from the general public (property managers, resident managers, strata owners, etc.) relating to fire prevention & fire protection issues. Advertising of services is prohibited.
Forum rules
Blatantly advertising your services is strictly prohibited. Violators will be banned from posting. Identification with a company engaged in providing fire equipment service is encouraged in order to validate responses (i.e. a "tag line" which states your name, company's name and contact information is allowed).

Annual Fire Inspection Class A Testing

Postby Frank » Tue Jan 26, 2016 7:07

Hello,
During the annual fire inspection is it required to test class A wiring loop coming
back to the fire panel, for open, short, and ground.

Thanks
Frank
 
Posts: 11
Joined: Tue Sep 03, 2013 4:36

Re: Annual Fire Inspection Class A Testing

Postby FIRETEK » Tue Feb 09, 2016 9:43

The "short" answer (pardon the pun) is ... yes!

Clause 6.6.1 Each data communication link (DCL) shall be tested to confirm that a trouble signal is received at the control unit or transponder under an open loop fault.

At the control unit:

6.2.2.1
F - Ground fault tested on positive and negative initiates a trouble signal;
R - Input circuit, alarm and supervisory operation, including audible and visual indication;
S - Input circuit supervision fault causes a trouble indication;
T - Output circuit supervision fault causes a trouble indication;...
Frank Kurz
http://www.firetechs.net
1 (888) 340-3473
FIRETEK
Site Admin
 
Posts: 69
Joined: Sat Aug 23, 2008 9:10
Location: Vancouver, B. C., Canada


Return to Ask a Tech!